    Hello Forum,
    I'm struggling to implement a PID controller for my oven. The sampling rate is dictated by the time to read a MAX6675, which is 0.25 seconds to complete a full conversion.
    The output should drive a homemade SSR, which using MOC3061 with ZCD. So I can only modulate the number of half sine wave on and off.
    As far as my researches I found the AN964, but the parameters are different so I don't get the idea how to convert the 360 degree from that note into 100 pulses per minute in my attempt.
    So the Kp, Ki and Kd can be an integer size and then there should be a divider to reduce them into fractional values. But the output should be from 0 to 100, with 250 mS time frame. So I'm puzzled to make the right corrections.

    Currently I just implement a proportional method and it seems to be rather enough, as fas as I simulated it.
    Code:
        Symbol MINTEMP  40                  ' minimum temperature level
        Symbol MAXTEMP 260                  ' maximum temperature level
        Symbol TEMPSPAN MAXTEMP - MINTEMP   ' temperature span
    
      Clear Result                      ' forget last state
      Clear AlarmFlag                   ' forget The flag
      If currtemp > Setpoint Then       ' when is over the Setpoint
        If currtemp > TEMPSPAN Then     ' may be over the guard limit
          Btfss no_PID                  ' when the flag is clear
          Set AlarmFlag                 ' it will signalize an error
        End If
        Return                          ' Stop there, return result zeroed
      End If
      If no_PID = TRUE Then             ' disable the proportional controller
        Set Result
        Return
      End If
      If currtemp > 0 Then              ' whether is higher than minimum temperature
        _PP2 = currtemp * 100/TEMPSPAN
        y = currtemp * KPD /Setpoint
        If ticks >= y.LowByte Then      ' the y higher the lesser ticks to stay on
          Set Result                    ' let fire the output
        End If
      Else                              ' in case it hasn't got to minimum level
        Set Result                      ' let the output to be on.
      End If
    EndProc
    I should say that the temperature is reduced to one byte, as far as the range is from 40 to 260C. When it's simulated I can see the oscillation is limited within 3 degrees, but when I trying the thermocouple it comes with a bigger hysteresis, that's why I suppose the PID would give a better solution.
    I found several pages, but all using floating point for the three constant Kp. Ki & Kd. I think I can do similar with integer values as long as using the method to multiply and divide with integers, such is done in that application note.

  2. Attention

    This valuable resource relies upon the very small amount of revenue generated by displaying online advertisements to our visitors.

    The advertisements we display are relevant to this web site and your browsing history

    Please consider supporting us by disabling your ad blocker.


    Note: Some users have reported issues related to ad-blockers rendering parts of this wesite unusable,
    where possible we will rectify the issues to enable you to use this resource with adblocking enabled.

    If you can, please report issues in the forum area WebSite / Forum Issues


    Thank you for your attention.

  3. #2
    Fanatical Contributor John Drew's Avatar
    Join Date
    Feb 2002
    Posts
    3,004
    Thumbs Up
    Received: 98
    Given: 34
    Total Downloaded
    5.17 GB

    0 Not allowed!

    Default Re: PID using integer math.

    Don't be afraid to use floating point. FP maths is sufficiently accurate for many applications and is very easy to use in Proton. Unless you're dealing with a tiny device at very low speed use FP if it makes your maths easier. I wouldn't hesitate. Unfortunately I didn't understand your abbreviations in the post.
    John

  4. Attention

    This valuable resource relies upon the very small amount of revenue generated by displaying online advertisements to our visitors.

    The advertisements we display are relevant to this web site and your browsing history

    Please consider supporting us by disabling your ad blocker.


    Note: Some users have reported issues related to ad-blockers rendering parts of this wesite unusable,
    where possible we will rectify the issues to enable you to use this resource with adblocking enabled.

    If you can, please report issues in the forum area WebSite / Forum Issues


    Thank you for your attention.

  5. #3
    Member keytapper's Avatar
    Join Date
    Jun 2019
    Posts
    323
    Thumbs Up
    Received: 13
    Given: 6
    Total Downloaded
    497.12 MB

    0 Not allowed!

    Default Re: PID using integer math.

    Thanks, John.
    I realized that the presented code is rather meaningless. The ZCD stands for Zero Crossing Detection.
    My intent is to remain on the tiny MCU, so here I'm to find what that application note is able to accomplish within few hundreds of instruction code.
    The above procedure evaluate the percentage to keep the TRIAC on or off, according the counter that is counting downward at every zero cross, which is sensed by the external interrupt. KPD is a correction constant to give a little better solution.
    Then in the main loop it will set the pin output according what the procedure result was comparing. The task in the main loop is carried out in less than 0.2 milliseconds and then there's plenty of idle time.

    The only part that I'm missing is how to scale down the output result in a number that should be from 0 to 100. Whereas the AN964 has a range from -180 to 180. Then I will be able to handle how many semi-waves to skip. There could be even a better way to distribute the OFF time in one second period, E.G. if the result si 10% it will be possible to skip 1 over 10, rather than 10 over 100. But this is another use case that in a tiny MCU will not fit.

    One thing I could decipher is that the three constant are read from the assembled potentiometers so the calculation will get the 10 bit ADC value and divide by 1024. The most relevant variables are SWord size, only the output is 32bit wide. But I still have room in my source for the RAM. I don't understand the scaling factor and perhaps the way I should take samples in a 2^n value, so the calculation will be just a bit shifting matter.
    Last edited by keytapper; 11th January 2021 at 14:08.

  6. Attention

    This valuable resource relies upon the very small amount of revenue generated by displaying online advertisements to our visitors.

    The advertisements we display are relevant to this web site and your browsing history

    Please consider supporting us by disabling your ad blocker.


    Note: Some users have reported issues related to ad-blockers rendering parts of this wesite unusable,
    where possible we will rectify the issues to enable you to use this resource with adblocking enabled.

    If you can, please report issues in the forum area WebSite / Forum Issues


    Thank you for your attention.

  7. #4
    Prolific Poster See_Mos's Avatar
    Join Date
    Feb 2004
    Posts
    1,368
    Thumbs Up
    Received: 20
    Given: 0
    Total Downloaded
    1.02 GB

    0 Not allowed!

    Default Re: PID using integer math.

    If I read your post correctly you are detecting every zero crossing?

    When using a zero crossing opto you do not need to detect zero crossing at all because the opto will take care of that. While opto LED is on it will drive both half cycles and in a worst case you will only miss one half cycle.

    Decide on a gate time. for a small heater it might be one second or for a very big heater it might be ten minutes. Some of the ones I worked on for nitrogen extractors were 65KW and the gate time was 10 minutes.

    Then just calculate the on and off times as a percentage of the gate time. If you use an interrupt timer for the gate that leaves plenty of time to take the sample and do the sums.

    Interestingly the end user could not understand why they could not run the nitrogen extractors on 110KVA generators. The company that built them had used phase angle control so at 50% heat requirement the generator was hit with a sudden current demand at the peak of the sine wave. The result was that the generator became very unstable, electrically and mechanically! The automatic voltage controller could not cope, the generators were going well over voltage and blowing 1500 volt voltage dependent resistors in the heater control.
    Last edited by See_Mos; 11th January 2021 at 16:10.
    My RAM is failing

  8. Attention

    This valuable resource relies upon the very small amount of revenue generated by displaying online advertisements to our visitors.

    The advertisements we display are relevant to this web site and your browsing history

    Please consider supporting us by disabling your ad blocker.


    Note: Some users have reported issues related to ad-blockers rendering parts of this wesite unusable,
    where possible we will rectify the issues to enable you to use this resource with adblocking enabled.

    If you can, please report issues in the forum area WebSite / Forum Issues


    Thank you for your attention.

  9. #5
    Member keytapper's Avatar
    Join Date
    Jun 2019
    Posts
    323
    Thumbs Up
    Received: 13
    Given: 6
    Total Downloaded
    497.12 MB

    0 Not allowed!

    Default Re: PID using integer math.

    Quote Originally Posted by See_Mos View Post
    If I read your post correctly you are detecting every zero crossing?

    When using a zero crossing opto you do not need to detect zero crossing at all because the opto will take care of that.
    I started by using the timer0 to count 10 mSec, the maximum permissible count, so I can use only one byte to measure one second. Because that is the part of the timer that I will use to set a heating period. I was worry that the TRIAC firing wasn't synchronize with the main. So I turned to use the count over the frequency main supply. Even the MOC3061 is with ZCD, so my best PWM is based on skipping some semi-wave.

    To have a regulated output I suppose to work on the skipped wave number. As the rectified waves are 100, therefore I consider to adjust the percentage that the TRIAC will stay on in a second.
    The MAX6675 needs at least 0.17 second for its ADC conversion. That implies the time frame won't be less than that, because the PID error calculation is possible only when a new sample is taken.
    To compare with the AN964 I need to understand what is the delta time to be used to calculate the integral and perhaps the derivative terms.

    I found a very informative page, I still need some more efforts to grasp the entire concept.

    The integral of a signal is the sum of all the instantaneous values that the signal has been, from whenever you started counting until you stop counting.
    This is the point where I should find the way to determine how long should be a time frame for my case. The two incognitos are when is time to take a sample and what is the relationship with 100 pulse per second (50 Hz x 2, from the main).

    I may guess that the degree per second might be about 5C/sec. Then I prepared a thermal switch at 260C, just to add further safety in case the system may be faulty. But the oven should go up to 250 and not higher. That is a particular condition that the PID controller won't have to exceed the set point for a long period.

  10. Attention

    This valuable resource relies upon the very small amount of revenue generated by displaying online advertisements to our visitors.

    The advertisements we display are relevant to this web site and your browsing history

    Please consider supporting us by disabling your ad blocker.


    Note: Some users have reported issues related to ad-blockers rendering parts of this wesite unusable,
    where possible we will rectify the issues to enable you to use this resource with adblocking enabled.

    If you can, please report issues in the forum area WebSite / Forum Issues


    Thank you for your attention.

  11. #6
    Member keytapper's Avatar
    Join Date
    Jun 2019
    Posts
    323
    Thumbs Up
    Received: 13
    Given: 6
    Total Downloaded
    497.12 MB

    0 Not allowed!

    Default Re: PID using integer math.

    One further step, I converted the AN964 source to proton basic
    Code:
    On_Interrupt GoTo interrupt_Isr
    Declare Xtal 8
    Device 16F684
    
    Symbol TRUE 1
    Symbol FALSE 0
    Symbol ADON = ADCON0.0                 ' A/D ON bit
    Symbol GO_DONE = ADCON0.1              ' A/D Conversion Enable
    Symbol CHS0 = ADCON0.2                 ' Analog Channel Select bits
    Symbol CHS1 = ADCON0.3                 ' Analog Channel Select bits
    Symbol CHS2 = ADCON0.4                 ' Analog Channel Select bits
    Symbol VCFG = ADCON0.6                 ' VCFG: Voltage Reference bit
    Symbol ADFM = ADCON0.7                 ' A/D Result Formed Select bit
    Symbol PS0 = OPTION_REG.0              ' Prescaler Rate Select
    Symbol PS1 = OPTION_REG.1              ' Prescaler Rate Select
    Symbol PS2 = OPTION_REG.2              ' Prescaler Rate Select
    Symbol PSA = OPTION_REG.3              ' Prescaler Assignment
    Symbol T0CS = OPTION_REG.5             ' TMR0 Clock Source Select
    Symbol ADCS0 = ADCON1.4             ' A/D Conversion Clock Select bit
    Symbol ADCS1 = ADCON1.5             ' A/D Conversion Clock Select bit
    Symbol ADCS2 = ADCON1.6             ' A/D Conversion Clock Select bit
    Symbol RAIF = INTCON.0               ' RA Port Interrupt Flag
    Symbol TMR0IF = INTCON.2             ' TMR0 Overflow Interrupt Flag
    Symbol INT0IE = INTCON.4             ' RA0 External Interrupt Enable
    Symbol TMR0IE = INTCON.5             ' TMR0 Overflow Interrupt Enable
    Symbol GIE = INTCON.7                ' Global Interrupt Enable
    Symbol ANS2 = ANSEL.2                 ' Pin Analog / Digital Selection
    Symbol ANS4 = ANSEL.4                 ' Pin Analog / Digital Selection
    Symbol ANS5 = ANSEL.5                 ' Pin Analog / Digital Selection
    Symbol IRCF0 = OSCCON.4             ' Internal Oscillator Frequency Select bits
    Symbol IRCF1 = OSCCON.5             ' Internal Oscillator Frequency Select bits
    Symbol IRCF2 = OSCCON.6             ' Internal Oscillator Frequency Select bits
    Symbol TMR2ON = T2CON.2              ' Timer2 ON
    Symbol DC1B0 = CCP1CON.4              ' PWM Duty Cycle Least Significant bits
    Symbol DC1B1 = CCP1CON.5              ' PWM Duty Cycle Least Significant bits
    Symbol P1M1 = CCP1CON.7               ' PWM Output Configuration bit
    Symbol RA4 = PORTA.4                   ' Bi-directional I/O pin (with interrupt on change)
    Symbol  SumE_Max = 30000
    Symbol  SumE_Min = 1 - SumE_Max
    
    Dim do_PID As Bit
    Dim ADchanel As ADRESL.Word
    Dim en0 As SByte
    Dim en1  As SByte
    Dim en2  As SByte
    Dim en3  As SByte
    Dim off_set  As SByte
    Dim temp As Byte
    Dim temp_int As SWord
    Dim ki As Word
    Dim kd As Word
    Dim kp As Word
    Dim SumE As SWord
    Dim integral_term As SWord
    Dim derivative_term As SWord
    Dim Cn As SDword
    
    main:
      Init()
      Set_Constants()
      Do
        If do_PID = TRUE Then
          PID()
        End If
      Loop
    End
    
    Sub Init()
      PORTA = 0
      TRISA = 101101
      PORTC = 0
      TRISC = 000011
      CMCON0 = $07
      IRCF0 = 1
      IRCF1 = 1
      IRCF2 = 1
      CCP1CON = 001100
      ECCPAS = 0
      PR2 = $3F
      T2CON = 0
      CCPR1L = 0
      TMR2ON = 1
      ANSEL = 110101
      VCFG = 0
      ADFM = 1
      ADCS0 = 1
      ADCS1 = 0
      ADCS2 = 1
      CHS0 = 0
      CHS1 = 0
      CHS2 = 0
      ADON = 1
    
      Clear en0
      Clear en1
      Clear en2
      Clear en3
      Clear ki
      Clear kd
      Clear kp
      Clear off_set
      Clear temp_int
      Clear integral_term
      Clear derivative_term
      do_PID = 1
      T0CS = 0
      TMR0 = 10
      PSA = 0
      PS0 = 0
      PS1 = 0
      PS2 = 1
      INTCON = 0
      PIE1 = 0
      TMR0IE = 1
      GIE = 1
    EndSub
    
    
    Sub PID()
      Clear integral_term
      Clear derivative_term
      SumE = SumE + en0
      If  SumE > SumE_Max Then
        SumE = SumE_Max
      End If
      If  SumE < SumE_Min Then
        SumE = SumE_Min
      End If
    
      integral_term = SumE / 256
      integral_term = integral_term * ki
      derivative_term = en0 - en3
      If  derivative_term > 120 Then
        derivative_term = 120
      End If
      If  derivative_term < -120 Then
        derivative_term = -120
      End If
    
      derivative_term = derivative_term * kd
      derivative_term = derivative_term >> 5
    
      If  derivative_term > 120 Then
        derivative_term = 120
      End If
      If  derivative_term < -120 Then
        derivative_term = -120
      End If
    
      Cn = en0 + integral_term + derivative_term
      Cn = Cn * kp / 1024
    
      If  Cn >= 1000 Then
        Cn = 1000
      End If
      If  Cn <= -1000 Then
        Cn = -1000
      End If
      If  Cn == 0 Then
        Clear DC1B1
        Clear DC1B1
        Clear CCPR1L
      End If
      If  Cn > 0 Then
        P1M1 = 0
        temp = Cn
        If  temp ^ 000001 = TRUE Then
          DC1B0 = 1
        Else
          DC1B0 = 0
        End If
        If  temp ^ 000010 = TRUE Then
          DC1B1 = 1
        Else
          DC1B1 = 0
        End If
        CCPR1L = Cn >> 2
        off_set = off_set +1
        If  off_set > 55 Then
          off_set = 55
        End If
      Else
        P1M1 = 1
        temp_int = Abs(Cn)
        temp = temp_int
        If temp ^ 000001 = TRUE Then
          DC1B0 = 1
        Else
          DC1B0 = 0
        End If
        If temp ^ 000010 = TRUE Then
          DC1B1 = 1
        Else
          DC1B1 = 0
        End If
        CCPR1L = temp_int >> 2
        off_set = off_set -1
        If  off_set < -55 Then
          off_set = -55
        End If
      End If
      en3 = en2
      en2 = en1
      en1 = en0
      en0 = 0
      do_PID = 0
      RA4 = 0
    EndSub
    
    Sub Set_Constants()
      ANS2 = 1
      ANS4 = 1
      ANS5 = 1
      ADFM = 1
      CHS0 = 0
      CHS1 = 0
      CHS2 = 1
      GO_DONE = 1
      While GO_DONE = TRUE
        DelayUS 20
      Wend
      ki = ADchanel
      CHS0 = 1
      CHS1 = 0
      CHS2 = 1
      GO_DONE = 1
      While GO_DONE = TRUE
        DelayUS 20
      Wend
      kd = ADchanel
      CHS0 = 0
      CHS1 = 1
      CHS2 = 0
      While GO_DONE = TRUE
        DelayUS 20
      Wend
      GO_DONE = 1
      kp = ADchanel
      CHS0 = 0
      CHS1 = 0
      CHS2 = 0
    EndSub
    
    interrupt_Isr:
      Context Save
      If TMR0IF = TRUE Then
        If TMR0IE = TRUE Then
          TMR0 = 10
          TMR0IF = 0
          RA4 = 1
          temp_int = ADchanel
          temp_int = temp_int - 512
          en0 = temp_int + off_set/8
          do_PID = 1
          GO_DONE = 1
        Else
          PIR1 = 0
          RAIF = 0
          INT0IE = 0
        End If
      End If
      If temp_int > 180 Then
        GoTo Clrvars
      End If
      If  temp_int < -180 Then
    Clrvars:
        Clear DC1B0
        Clear DC1B1
        Clear CCPR1L
        Clear en0
        Clear en1
        Clear en2
        Clear en3
        Clear off_set
        Clear Cn
        Clear integral_term
        Clear derivative_term
        Clear SumE
        Clear RA4
        Clear do_PID
      End If
      Context Restore
    So I could figure out the resulting volume of the assembly. Definitely there will be less operations and no Analog input to add. Perhap the three constant will go on the EEPROM.
    The original source seems to me that had no much optimization, but it fits in less than 1 Kwords.

  12. Attention

    This valuable resource relies upon the very small amount of revenue generated by displaying online advertisements to our visitors.

    The advertisements we display are relevant to this web site and your browsing history

    Please consider supporting us by disabling your ad blocker.


    Note: Some users have reported issues related to ad-blockers rendering parts of this wesite unusable,
    where possible we will rectify the issues to enable you to use this resource with adblocking enabled.

    If you can, please report issues in the forum area WebSite / Forum Issues


    Thank you for your attention.

  13. #7
    Fanatical Contributor top204's Avatar
    Join Date
    Feb 2002
    Posts
    3,897
    Thumbs Up
    Received: 385
    Given: 196
    Total Downloaded
    2.09 GB

    0 Not allowed!

    Default Re: PID using integer math.

    With most controls, the full PID is not required, and can be slow to respond.

    I have, generally, used a PI method, where the error is stored and then the output is altered until the error is 0, or close to it.

    I created a PID control for a constant current source when plating copper, but even on a dsPIC33, the initial response from the PID was slow, until it had matched close to what it should be, which casues rough surfaces on the copper plating, so I changed it to a simple error offset mechanism and it worked much better, and the volume of heat and fluid made the current changes slow to alter, so full PID was not required.

  14. Attention

    This valuable resource relies upon the very small amount of revenue generated by displaying online advertisements to our visitors.

    The advertisements we display are relevant to this web site and your browsing history

    Please consider supporting us by disabling your ad blocker.


    Note: Some users have reported issues related to ad-blockers rendering parts of this wesite unusable,
    where possible we will rectify the issues to enable you to use this resource with adblocking enabled.

    If you can, please report issues in the forum area WebSite / Forum Issues


    Thank you for your attention.

  15. #8
    Prolific Poster See_Mos's Avatar
    Join Date
    Feb 2004
    Posts
    1,368
    Thumbs Up
    Received: 20
    Given: 0
    Total Downloaded
    1.02 GB

    0 Not allowed!

    Default Re: PID using integer math.

    For a small AC oven heater control using BURST FIRE CONTROL I would start with a gate period of ten seconds. Divide the period by 100 to give tenth of a second control which is equal to a minimum of four and a half or five cycles ON time at 50Hz depending on when the MOC3061 LED is turned on

    Any finer resolution would be a waste of processing time.
    My RAM is failing

  16. Attention

    This valuable resource relies upon the very small amount of revenue generated by displaying online advertisements to our visitors.

    The advertisements we display are relevant to this web site and your browsing history

    Please consider supporting us by disabling your ad blocker.


    Note: Some users have reported issues related to ad-blockers rendering parts of this wesite unusable,
    where possible we will rectify the issues to enable you to use this resource with adblocking enabled.

    If you can, please report issues in the forum area WebSite / Forum Issues


    Thank you for your attention.

  17. #9
    Member keytapper's Avatar
    Join Date
    Jun 2019
    Posts
    323
    Thumbs Up
    Received: 13
    Given: 6
    Total Downloaded
    497.12 MB

    0 Not allowed!

    Default Re: PID using integer math.

    Forgive my lack of knowledge.
    I'm trying con conceive how to write the formula.
    I'm seeing that one degree increase may take a couple of seconds. So I agreed that the time frame may be 10 seconds long. During this period I can keep the ON_time of the TRIAC as the result of the calculation will give.

    My concern is about keeping the tolerance within +/- 2 degree, otherwise it would not make sense to set the temperature and see 10% variations.

    Maybe Fanie's wife got some experience about carbonized foods .

    @ Les
    I tried the simple ON/OFF control but I'm getting an horrible 8~10% variations around the set point.
    I tried a proportional control which reduces the power factor as soon as the temperature is close to the set point. The simulation promising a 1% variation, but the hardware won't reach the set point at all.
    Last edited by keytapper; 12th January 2021 at 15:51.

  18. Attention

    This valuable resource relies upon the very small amount of revenue generated by displaying online advertisements to our visitors.

    The advertisements we display are relevant to this web site and your browsing history

    Please consider supporting us by disabling your ad blocker.


    Note: Some users have reported issues related to ad-blockers rendering parts of this wesite unusable,
    where possible we will rectify the issues to enable you to use this resource with adblocking enabled.

    If you can, please report issues in the forum area WebSite / Forum Issues


    Thank you for your attention.

  19. #10
    Prolific Poster See_Mos's Avatar
    Join Date
    Feb 2004
    Posts
    1,368
    Thumbs Up
    Received: 20
    Given: 0
    Total Downloaded
    1.02 GB

    0 Not allowed!

    Default Re: PID using integer math.

    Yes, I was thinking again. Ten seconds might be too long so maybe one second but then the MAX6675 is a problem.
    My RAM is failing

  20. Attention

    This valuable resource relies upon the very small amount of revenue generated by displaying online advertisements to our visitors.

    The advertisements we display are relevant to this web site and your browsing history

    Please consider supporting us by disabling your ad blocker.


    Note: Some users have reported issues related to ad-blockers rendering parts of this wesite unusable,
    where possible we will rectify the issues to enable you to use this resource with adblocking enabled.

    If you can, please report issues in the forum area WebSite / Forum Issues


    Thank you for your attention.

  21. #11
    Member keytapper's Avatar
    Join Date
    Jun 2019
    Posts
    323
    Thumbs Up
    Received: 13
    Given: 6
    Total Downloaded
    497.12 MB

    0 Not allowed!

    Default Re: PID using integer math.

    Quote Originally Posted by See_Mos View Post
    one second but then the MAX6675 is a problem.
    The max6675 needs 0.17 seconds (typical) to do a full conversion. I set for 0.25 seconds, so that's the minimum time frame and it rounds up with 4 samples per second.

  22. Attention

    This valuable resource relies upon the very small amount of revenue generated by displaying online advertisements to our visitors.

    The advertisements we display are relevant to this web site and your browsing history

    Please consider supporting us by disabling your ad blocker.


    Note: Some users have reported issues related to ad-blockers rendering parts of this wesite unusable,
    where possible we will rectify the issues to enable you to use this resource with adblocking enabled.

    If you can, please report issues in the forum area WebSite / Forum Issues


    Thank you for your attention.

  23. #12
    Prolific Poster See_Mos's Avatar
    Join Date
    Feb 2004
    Posts
    1,368
    Thumbs Up
    Received: 20
    Given: 0
    Total Downloaded
    1.02 GB

    0 Not allowed!

    Default Re: PID using integer math.

    You are correct, after posting I read the data sheet and it only takes about 3.2mS to read the information and typically 170mS while the device does the conversion so if you only take one or two readings a second there is plenty of time to do the maths and do the rest.

    Unfortunately maths is my weakness so cannot help there.
    My RAM is failing

  24. Attention

    This valuable resource relies upon the very small amount of revenue generated by displaying online advertisements to our visitors.

    The advertisements we display are relevant to this web site and your browsing history

    Please consider supporting us by disabling your ad blocker.


    Note: Some users have reported issues related to ad-blockers rendering parts of this wesite unusable,
    where possible we will rectify the issues to enable you to use this resource with adblocking enabled.

    If you can, please report issues in the forum area WebSite / Forum Issues


    Thank you for your attention.

  25. #13
    Member keytapper's Avatar
    Join Date
    Jun 2019
    Posts
    323
    Thumbs Up
    Received: 13
    Given: 6
    Total Downloaded
    497.12 MB

    0 Not allowed!

    Default Re: PID using integer math.

    I am studying all day how to whip up the formula. Roughly it cost some 400 words. But I can't get the correct scaling to set the PWM for the TRIAC. In fact the TRIAC should keep on a modulated percentage until a new reading arrive.
    Compare to those formulas I saw on the web, the time frame is not necessary whenever it's working in a constant rate. So as I may guess the procedure may be a couple of second long, in that time the temperature doesn't vary that much. Even doing with 0.01 seconds I still have lot of idle time at 20 MHz clock.

    A very rough design is as follow:

    Code:
    Device 16F628A
    Declare Xtal 20
    
    Symbol Kp 1298
    Symbol Ki 987
    Symbol Kd 14
    Symbol DeltaTime 10
    ' rough figure in mills. Better in binary value to reduce calculation in a shift right.
    $define fractionOf(x) x / 1024 
    
    Dim err As SByte
    Dim previous_error As SByte
    Dim derivative As SByte
    Dim integral As SWord
    Dim PIDout As SByte
    Dim tmp As SDword
    Dim currtemp As Byte
    Dim Setpoint As Byte
    
    Do
      err = Setpoint - currtemp
      tmp = err * fractionOf(Kp)
      integral = integral + err*DeltaTime
      If integral > 32000 Then integral = 32000
      If integral < -32000 Then integral = -32000
      tmp = tmp + integral * fractionOf(Ki)
      derivative = (err - previous_error)/DeltaTime
      tmp = tmp + derivative * fractionOf(Kd)
      If tmp > 100 Then tmp = 100
      If tmp < 0 Then tmp = 0
      PIDout = tmp
      previous_error = err
      DelayMS DeltaTime
    Loop
    If sampling rate is constant, then the DeltaTime is 1, therefore may be eliminated.
    Thus it's like the bloggers suggest, but I don't realize how to adjust the output in the correct scaling which will give the T_ON and T_OFF for the TRIAC. I'm facing a huge jump on the integral that it won't recover. Also the output starts to reduce very early.

  26. Attention

    This valuable resource relies upon the very small amount of revenue generated by displaying online advertisements to our visitors.

    The advertisements we display are relevant to this web site and your browsing history

    Please consider supporting us by disabling your ad blocker.


    Note: Some users have reported issues related to ad-blockers rendering parts of this wesite unusable,
    where possible we will rectify the issues to enable you to use this resource with adblocking enabled.

    If you can, please report issues in the forum area WebSite / Forum Issues


    Thank you for your attention.

  27. #14
    Member keytapper's Avatar
    Join Date
    Jun 2019
    Posts
    323
    Thumbs Up
    Received: 13
    Given: 6
    Total Downloaded
    497.12 MB

    0 Not allowed!

    Default Re: PID using integer math.

    I think the algorithm works. It just take in account that the procedure should follow the response time of what is measured. like this page mention, the sampling would be about 10 time smaller than the measure variation. Thus when the variation may be 15 second per degree, the sample shouldn't be smaller than 1.5 second, otherwise the integral variable will reach its limits without any chance to recover.
    There's just a nasty situation when starting that cause an overshooting. That seems normal, as many pages reporting.

    I just try the algorithm with the simulator, the result is pretty like what I expect. Tomorrow I'll try with my hardware simulation.

  28. Attention

    This valuable resource relies upon the very small amount of revenue generated by displaying online advertisements to our visitors.

    The advertisements we display are relevant to this web site and your browsing history

    Please consider supporting us by disabling your ad blocker.


    Note: Some users have reported issues related to ad-blockers rendering parts of this wesite unusable,
    where possible we will rectify the issues to enable you to use this resource with adblocking enabled.

    If you can, please report issues in the forum area WebSite / Forum Issues


    Thank you for your attention.

  29. #15
    Senior Member Ken_K's Avatar
    Join Date
    Aug 2007
    Posts
    454
    Thumbs Up
    Received: 7
    Given: 2
    Total Downloaded
    529.65 MB

    0 Not allowed!

    Default Re: PID using integer math.

    A most interesting topic, I did not see the C code for the app note 964 so I re posted it here.

    http://read.pudn.com/downloads37/sou...ndulum.c__.htm

    and the pendulum app note again

    http://ww1.microchip.com/downloads/en/Appnotes/00964A.pdf

    T
    hese are worth saving and are now in my library.

  30. Attention

    This valuable resource relies upon the very small amount of revenue generated by displaying online advertisements to our visitors.

    The advertisements we display are relevant to this web site and your browsing history

    Please consider supporting us by disabling your ad blocker.


    Note: Some users have reported issues related to ad-blockers rendering parts of this wesite unusable,
    where possible we will rectify the issues to enable you to use this resource with adblocking enabled.

    If you can, please report issues in the forum area WebSite / Forum Issues


    Thank you for your attention.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

     

Similar Threads

  1. 64 Bits Integer Math
    By AlbertoFS in forum Proton Plus Compiler v3
    Replies: 14
    Last Post: 12th July 2014, 11:59
  2. integer log logarithm?
    By cgriffin in forum Proton Plus Compiler v3
    Replies: 5
    Last Post: 5th December 2009, 20:46
  3. [SOLVED !] reconized integer in float
    By Roshan in forum Proton Plus Compiler v3
    Replies: 4
    Last Post: 31st August 2008, 14:47
  4. [SOLVED !] Converting Float to integer
    By RIKUS in forum Proton Plus Compiler v3
    Replies: 3
    Last Post: 7th November 2006, 07:56
  5. [SOLVED !] Floating point math? 32 bit Math?
    By AlienRelics in forum Wish List / Product Feedback
    Replies: 0
    Last Post: 5th July 2002, 00:57

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts